(Topic ID: 185634)
Help: Solenoid Expander Weak Right Kickback
By magacod
7 years ago
#1 7 years ago
Blackbelt specifically. The Right Kickback is sometimes weak. It only occurs for a few seconds after the Right side or Left side switch gates are activated, the ones opposite the top two flippers. When this happens the relay makes a buzzing noise if the kickback is activated soon afterwards. No issues with anything else controlled by the solenoid expander. And the kickback functions normally during the rest of play, no buzzing, powerful.
The switch for the kickback isn't on the same row or column as the gates in the switch matrix.
The lights activated by the gates are the Normally Closed side of the Solenoid Expander
The Kickback is on the Normally Open side.
The diodes on the 48v wire the Top Left Lights and the Kickback share have been replaced.
The Solenoid Expander light is working perfectly.
I suspect it's undervolted when all of the lights are on, however i'd expect the other solenoids on the Normally Open side to act the same in the same situation and they do not.
I'm mostly just wondering if this is a design issue as opposed to a failure. However, a previous owner managed to set most of the solenoid flasher lights on fire. It's actually quite impressive.
#2 7 years ago
Hi megacod - I'm not sure of the answer to your question. I'm working on a BB myself that also had flashers on fire, as well as a variety of other rough treatments (playfield apparently rewired?).
I suspect that the game has to change the state of the relay really quickly and there's not enough time or a switch needs to be cleaned or adjusted within the relay - or you're just fighting physics.
Would you be willing to take a few pics of the area near your SEB for my reference? To be specific, I'm looking for any diodes that are mounted near or feeding the SEB. Sorry to clutter your thread with my request.
#3 7 years ago
Yours will look be arranged differently. In testing the Solenoid Expander I re-mounted the lugs, added more and spaced them out more. It was too easy for wires to touch, which seems to be common for this playfield. I meant to redo this to make it a little neater, oh well.
My diodes were backfeeding and blowing the 11v fuses. I replaced those and IIRC I was missing the diode on the bottom. Also quite a few more diodes were backfeeding throughout the playfield. I imagine we had a similar failed component to cause the fires.
#4 7 years ago
ah ha! Yep - that's all missing and was miswired, which was causing the 11V fuses to blow over here as well. Explains a lot. Thank you.
#5 7 years ago
Does your relay buzz in test mode in the all lamps test?
#6 7 years ago
I'm using one of the aftermarket boards and have not noticed it buzzing, but it uses a solid state relay instead of the original design. I don't know that I'd be able to hear it if it was buzzing.
Once I am back in front of the game and rewire the SEB lamp/diodes, I'll see if I can replicate your problem. I may not be able to, again, due to the change in design of the SEB.
#7 7 years ago
I am having the same issue with the kick out. I posted what I have found on KLOV. I noticed the original diodes on the bright lights are a "GE A14A", I have a few ordered to install and try. The manual says the lamp and coil diodes are 1N4004. If I take the 3 bulbs out of the top left string, it seems to work fine. All my coils are getting about 24 volts. This is the last non working issue with the Black Belt.
#8 7 years ago
Replaced connector J9. All good now.
#9 7 years ago
I fixed mine by just applying contact cleaner liberally to related connections and the relay.
#10 6 years ago
Did this issue stay solved for you guys or has it returned?
I have the EXACT same issue on a Black Belt. Intermittent weak top right kicker. Seems to happen more often when left and right ramp switches are hit just before.
New solenoid expander board, new connector and reflow at J9, issue remains here...
#11 6 years ago
I am still having the same issue. New coil, SEB, replaced diodes on all coils and bright lights. The right ramp switch will make it fail. It seems to happen more if you have 2 or 3 belts.
#12 6 years ago
Mine did work correctly for about a week after I applied contact cleaner to the inside of the relay and connector pins on the relay, but I did a lot of other things during the same time period.
I'm assuming yours' also will fire weakly about three times in a row then put out a full strength shot, and this only happens for about 10 seconds after the right gate is activated.
My next steps are to:
Remove a top left solenoid light, check effects.
Check condition of FU1 5A fuse.
Check condition of playfield fuse.
Check TP4 voltage. 43vdc out vs 49vac in
Replace the bulb on the solenoid expander with the highest and lowest resistance bulbs i have.
Check voltage and amperage going to coil after the right gate switch gets activated follow by the kickback switch.
Clip the capacitor on the right gate switch, check effects.
Install a capacitor on the kickback switch
Replace diodes on the coil
?Replace the coil with one that needs less voltage.
?Install a capacitor on the kickback coil.
?It could be that a 43v Capacitor is nearing failure. I don't see a capacitor on the schematics. It doesn't look like the 43vdc output has a capacitor. However, nothing else has power issues anyway. If anything the 43v line is too strong.
?There is a 48v relay on the pinball control module. I think it's unrelated.
Does anyone have a new power supply or transformer? Or both?
#13 6 years ago
Quoted from magacod:
That's an exact description. Although it's not every single time.
Seems like a good list. Let us know if you get through any of the steps.
I have:
- Replaced SEB board
- New connector and re-flow at MPU J9
- Removed (LED's) from the top left series bright lights (same transistor, other SEB phase)
One other thought... Does your game include the Bally "bright lights field kit"? See pics below. I'm wondering if this kit may be contributing to the issue... I noticed mine is wired with the resistor before the fuse, not after as instructed.
#14 6 years ago
x - (No effect) Remove a top left solenoid light, check effects.
x - (Fine) Check condition of FU1 5A fuse.
x - (Fine) Check condition of playfield fuse.
x - (Perfect) Check TP4 voltage. 43vdc out vs 49vac in
x - (No change, left an LED in) Replace the bulb on the solenoid expander with the highest and lowest resistance bulbs i have.
x - (I removed the solenoid expander bulb and nothing changed, very strange)
x - (Amperage is lower after a right gate activation, even if the relay seems to work correctly. Measuring voltage makes it so the relay never properly latches) Check voltage and amperage going to coil after the right gate switch gets activated follow by the kickback switch.
x - (Already did this) Replace diodes on the coil
- Clip the capacitor on the right gate switch, check effects.
- Install a capacitor on the kickback switch
? - Replace the coil with one that needs less voltage.
? - Install a capacitor on the kickback coil.
? - It could be that a 43v Capacitor is nearing failure. I don't see a capacitor on the schematics. It doesn't look like the 43vdc output has a capacitor. However, nothing else has power issues anyway. If anything the 43v line is too strong.
? - There is a 48v relay on the pinball control module. I think it's unrelated.
? - Does anyone have a new power supply or transformer? Or both?
- Remove right side and 20k lamps
- Replace right side and 20k lamp diodes.
Other operators efforts:
x - Replaced SEB board
x - New connector and re-flow at MPU J9
x - Removed (LED's) from the top left series bright lights (same transistor, other SEB phase)
Repair guide:
http://www.techniek.flipperwinkel.nl/ballyss/rep/index3.htm#expand
Done - Header pins on the solenoid expander board may have cracked solder joints. Re-flow these header pin solder joints.Done - In-series diode going to the power lug of the coil may be broken, missing or reversed.
Done - Diode across the lugs of the coil may be broken, missing or reversed.
Done - Switch contacts on the solenoid expander board's relay may be pitted and may need to be filed (or the relay replaced).
Done - The solenoid expander board's MOC3011 opto-isolator may be bad. Replacements are available from Jameco (part #95020), or replace with NTE3047.
Done - Diode on the solenoid expander board's relay may be broken or missing.
Doubtful - The lamp under the playfield next to the solenoid expander board may be burned out. Replace with a new lamp. Without this lamp, there isn't enough load for the SCR on the lamp driver board to activate the solenoid expander board's relay.
Doubtful - The lamp driver board's SCR that controls the solenoid expander board may have failed. See Locked-On or Not Working Feature Lights (lamp driver board) section for details on how to test the SCR.
- The 6.5 volts provided by the power supply's rectifier board BR1 bridge may be failing. The 6.5 volts DC provided by BR1 powers the
- feature lamps. If this voltage is low, the solenoid expander board's relay may not function correctly.
- The power supply's rectifier board R2 resistor (25 ohms 5 watts) may be broken or open. Check it with your DMM set to ohms.
- Connector pins on the power supply's rectifier board may be burned or tarnished. This will create resistance which will lower the 6.5 volts DC provided to the lamp driver board. If this voltage is low, the solenoid expander board's relay may not function correctly.
comments:
The relay isn't latching properly when the relay fails to fully activate the coil. The relay sparks and hums.
The relay still doesn't latch correctly with the kickback coil detached.
Problem is likely then related to the relay or SEB board.
A lot of you have replaced both, so it's not necessarily that.
Bad transistor?
The other solenoids are slightly leaky, about 0.01 amps were measured going through kickback coil when other solenoids were activated. But this is probably normal.
I don't have the Bright Lights Field Kit, Although I might install one now (Does your playfield have any scorch marks?)
I've tried everything I can think of to get a similar failure for another solenoid, hasn't happened.
#15 6 years ago
Updated 5/5
x - (I removed the solenoid expander bulb and nothing changed, everything was still functional, very strange)
x - (done) Replace diodes on the coil
x - (no change) Clip the capacitor on the right gate switch, check effects.
x - (no change) Install a capacitor on the kickback switch
? - (doubtful) Replace the coil with one that needs less voltage.
? - (doubtful) Install a capacitor on the kickback coil.
? - (doubtful) It could be that a 43v Capacitor is nearing failure. I don't see a capacitor on the schematics. It doesn't look like the 43vdc output has a capacitor. However, nothing else has power issues anyway. If anything the 43v line is too strong.
? - (doubtful) There is a 48v relay on the pinball control module. I think it's unrelated.
x - (no change) Remove right side and 20k lamps
x - (doubtful) Replace right side and 20k lamp diodes.
x - (seems like no change) add a lamp in series with solenoid expander after phase a/b line diodes and before pin connection to SEB
X - (measured 6.4) check 6.3vac voltage
tbd - check connectors between all lamp related parts. i know i sprayed them with contact cleaner, seeming like this is it.
x - Installed bright lights field kit
Repair guide:
x - (done) Header pins on the solenoid expander board may have cracked solder joints. Re-flow these header pin solder joints.Done - In-series diode going to the power lug of the coil may be broken, missing or reversed.
x - (done) Diode across the lugs of the coil may be broken, missing or reversed.
x - (done) Switch contacts on the solenoid expander board's relay may be pitted and may need to be filed (or the relay replaced).
x - (done) The solenoid expander board's MOC3011 opto-isolator may be bad. Replacements are available from Jameco (part #95020), or replace with NTE3047.
x - (done) Diode on the solenoid expander board's relay may be broken or missing.
x - (done) The lamp under the playfield next to the solenoid expander board may be burned out. Replace with a new lamp. Without this lamp, there isn't enough load for the SCR on the lamp driver board to activate the solenoid expander board's relay.
tbd - The lamp driver board's SCR that controls the solenoid expander board may have failed. See Locked-On or Not Working Feature Lights (lamp driver board) section for details on how to test the SCR.
tbd - The 6.5 volts provided by the power supply's rectifier board BR1 bridge may be failing. The 6.5 volts DC provided by BR1 powers the feature lamps. If this voltage is low, the solenoid expander board's relay may not function correctly.
tbd - The power supply's rectifier board R2 resistor (25 ohms 5 watts) may be broken or open. Check it with your DMM set to ohms.
tbd - Connector pins on the power supply's rectifier board may be burned or tarnished. This will create resistance which will lower the 6.5 volts DC provided to the lamp driver board. If this voltage is low, the solenoid expander board's relay may not function correctly.
Comments:
Problem is likely then related to the relay or SEB board or something before it.
Bad transistor?
I think this is related to a lamp or something that controls a lamp
Update 5/5 #2
With only the lamp driver and 48v power going into and out of the relay it still has the same failure related to the right gate.
I have only pins 1,2,3, and 9 connected.
It doesn't spark as much but it still doesn't properly latch. Problem is definitely not a solenoid or anything on the NO or NC circuits.
Update 5/5 #3
Problem is almost certainly insufficient current/voltage to activate the relay.
#16 6 years ago
Thanks for working on this. You may want to un-check "solved" for this thread.
I replaced power board BR1 and experienced no change. I may throw a new transistor at it tomorrow to rule that out as well.
I can also make the kick-out weak by activating the left ramp switch. I believe both ramp switches activate the top-left bright lights which share the transistor with the kickout (different SEB phases).
I do see major scorch marks / burnt wood on the single center bright light underneath the man. It's unknown if that happened before or after the bright lights field kit. Now it has LED's so that should no longer be an issue.
Although we have identical symptoms, let me know if I can assist by comparing voltages, etc. I'll be working on it this weekend.
#17 6 years ago
x - new transistor at Q19. No change.
Issue remains and is easily reproducible by hitting the right OR left ramp switches immediately before the ball lands at the kicker.
#18 6 years ago
Try removing the 3 bright lights in the top left string. I installed New rom. Issue remains.
#19 6 years ago
That was one of the first things I tried...
#20 6 years ago
It's an issue with the lamp part of the circuit. If the solenoid expander is disconnected the lamp still won't flash at full brightness when the right gate is activated.
The misfire only happens when the top left flasher flashes. There seems to be little rhyme or reason as to when or why the top left flashers flash. They don't always flash after a right gate activation and don't always flash with the kickback, but they sometimes do and this causes the issue.
The coils and flashers controlled by the solenoid expander will fire even if their lamp phase is disconnected. This shouldn't be possible. When a phase is disconnected the relay then just tries to latch to both the NC and NO side at the same time.
New list of possible issues in order of likelihood:
Leaky flash/feature lamp diode (There's only 50+ to swap)
****There's probably a clever way to test this. I think disconnect CJ10, CJ11, and CJ13 and then jumper CJ10-6 from the connector
Insufficient voltage to lamp driver board (dirty pin or broken connector/solder)
Failed lamp driver SCR
Timing/clock/crystal failed
Bad programming/design
#21 6 years ago
I disconnected all the flash lamps besides the solenoid expander and still had the same issue with the relay not properly switching between NO and NC.
I grounded the MPU screws using physical wire instead of using the foil covered cardboard or whatever is in the backbox. No change.
I don't think it's a power issue or a failed SCR because it only occurs when the top left flasher and kickback are activated at the same time. But this is what I'm checking next.
I still don't understand how the kickback/saucers can even attempt to fire when their phase is disconnected. Although it is AC and the waveform is analog, so maybe the SCR is just reading the low/dissipating voltage and firing anyway.
I doubt the lamp next to the SEB is necessary anymore considering how much resistance our dirty connectors are causing. If anything the SEB probably needs the extra amps. But this is just a thought.
I think the easy solution is going to be delaying the right kick back activation signal somehow.
#22 6 years ago
I took it apart to clear coat the playfield. so the resolution to this is going to be a little delayed.
4 months later
#23 6 years ago
I swapped the kickback coil with the knocker coil. It works well enough. Don't forget to add a diode if you do that. I doubt I'm going to figure out a better solution.
9 months later
#24 5 years ago
Did anyone solve this issue? I swapped the knocker coil and no change. I also installed a new control board.
$ 32.00
$ 9.95
$ 18.95
This page was printed from https://pinside.com/pinball/forum/topic/help-solenoid-expander-weak-right-kickback and we tried optimising it for printing. Some page elements may have been deliberately hidden.
