Thanks Guys, I appreciate the help! I thought somthing was amiss with the wiring. I an not surprised as the switch dog question in another thread was in the wrong position at 2C. I still not up to speed on reading the schematic and therefore not always confident in my interpretation. So once again thanks for all of your help.
Mark:
If you compare against the schematic you can see that the blue-white-red wire (1) comes into the top of the frame to the P4E switch. Check.
(Phil's response: solder joints look good and the connection as 0 ohms.
On the other side of the P4E switch the orange-white-red wire (2) leaves the other side of the P4E switch. Check.
(Phil's response: Checks OK)
And further down you can see the brown-white-red (3) wire leaves one side of the P3E switch. Check.
(Phil's response: Checks OK-leaves top tab next to P2)
However,
- the orange-red-white wire (2) should go to the other side of the P3E switch.
- the P3E switch appears to have its solder lugs shorted together.
(Phil's response: Yes they are. This is what confused me and my resulting question. At your suggestion, I de-solder the connection between P4E and P4E.
I then connected a jumper between the orange-red-white wire (2) to the other side of the P3E switch. I then initiated a start up sequence. Both Player Score Reels now re-set to zero.) YAH!
- that blue jumper wire goes somewhere it probably shouldn't. It should maybe go to the orange-white-red (2) wire on switch P4E instead?
(Phil's Response: the blue jumper is between P1 and P2. Teh picture doesn't show this clearly. I left it alone for now).
If the P3E switch is really shorted, it seems that the player 1 score reels might not reset properly.
(Phil' Respnse: you are correct. Player One Score Reels did not reset. They do not after removing the dead short and connection P3E to P4E via the orange-red-white wire).
Guard thanks for the picture as I do find them helpful.
Now I have to figure out way the U relay does not de-energize upon AX energizes. I'll start a different thread for that.
Thanks Much!
Phil
